Chris Pearson:
I have a couple of SRCDs. The manufacturer's instructions say that the product should be removed from the circuit prior to insulation resistance testing. That's fine if you have only one in a ring, it's on a spur, or is at the end of a radial circuit, but a bit of a problem otherwise.
You've got to ask whether that's fit for purpose in a BS 7671 installation at the present time ... but perhaps an indicator of the way things will change in future.