AMD 2 - insulation testing

Looks like the DPC has made a bit of a change about insulation testing where some devices might be vulnerable to a 500V test voltage or distort the results. Previously we were allowed to either disconnect the item concerned (or do the test prior to initial connection) OR carry out a 250V test (with a 1MΩ limit to meet).


As I read it, a full 500V test will soon be required prior to connection of such equipment PLUS an additional 250V test (with a 1MΩ limit to meet) will be required after it is connected.


I can see the sense in that, in that it doesn't 'excuse' the rest of the circuit from a full 500V test, but I'm slightly uneasy about some equipment not being happy with a relatively long duration 250V d.c. test L&N - PE - especially if it has to meet a 1MΩ limit. Does anyone have any thoughts on that?


All strictly speaking for an initial verification - for a periodic we still seem to have the flexibility of choosing 'appropriate' tests (however that's going to be interpreted...).


Seems it's going to be a bit of extra work, especially if you've a house full of USB power sockets....


   - Andy.
Parents
  • Around twenty years ago I was repositioning a cooker circuit in an uncompleted barn conversion, the electrical installation had been completed, but I was installing the first ever kitchen in the new home.


    There was a cooker switch with a neon, so I tested each half of the circuit live to neutral with the switch disconnected, then refitted the switch and did live to earth of the whole circuit with it in place. When I turned the power on the switch literally blew up as it had a dead short in it.


    You just cannot win them all!
Reply
  • Around twenty years ago I was repositioning a cooker circuit in an uncompleted barn conversion, the electrical installation had been completed, but I was installing the first ever kitchen in the new home.


    There was a cooker switch with a neon, so I tested each half of the circuit live to neutral with the switch disconnected, then refitted the switch and did live to earth of the whole circuit with it in place. When I turned the power on the switch literally blew up as it had a dead short in it.


    You just cannot win them all!
Children
No Data