AJJewsbury:
Thanks Graham - that looks similar to my earlier attempt. I'll give it some thought...
Superficially though it doesn't look too bad against the figures I've got for MCBs - at 3kA
B16 15,000A²s
C16 18,000A²s
C20 22,000A²s
B32 18,000A²s
(which also suggest a 1.0mm² conductor (with a k²S² of 13,225) isn't protected)
I understand that our continental cousins typically prefer C types for their socket circuits - so if anything our B32 look like a better choice.
- Andy.
Those figures look like they're from the standard ... but the Type C ones are too high at 3 kA
The figures for let-through at 3 kA fault current, from the current standard are:
In reality, mcb's will have let-through much lower than BS EN 60898 / BS EN 61009.
AJJewsbury:
Thanks Graham - that looks similar to my earlier attempt. I'll give it some thought...
Superficially though it doesn't look too bad against the figures I've got for MCBs - at 3kA
B16 15,000A²s
C16 18,000A²s
C20 22,000A²s
B32 18,000A²s
(which also suggest a 1.0mm² conductor (with a k²S² of 13,225) isn't protected)
I understand that our continental cousins typically prefer C types for their socket circuits - so if anything our B32 look like a better choice.
- Andy.
Those figures look like they're from the standard ... but the Type C ones are too high at 3 kA
The figures for let-through at 3 kA fault current, from the current standard are:
In reality, mcb's will have let-through much lower than BS EN 60898 / BS EN 61009.