Sparkingchip:
What sort of question is that to ask of a guy with a lightning charger lead dangling over the arm of the settee immediately next to him?
Being an Ipad lightning lead the terminals are exposed to touch and every so often I feel a tingle when I put by bare elbow on it, guess what it is plugged into?
So the worst that can happen is?
Sparkingchip:Sparkingchip:
What sort of question is that to ask of a guy with a lightning charger lead dangling over the arm of the settee immediately next to him?
Being an Ipad lightning lead the terminals are exposed to touch and every so often I feel a tingle when I put by bare elbow on it, guess what it is plugged into?
So the worst that can happen is?
Depends what's causing the tingles. In terms of failure of protection against fault current, well, if there's a fault, but inadequate protection, the worst is fire and/or small explosion I guess.
Sparkingchip:Sparkingchip:
What sort of question is that to ask of a guy with a lightning charger lead dangling over the arm of the settee immediately next to him?
Being an Ipad lightning lead the terminals are exposed to touch and every so often I feel a tingle when I put by bare elbow on it, guess what it is plugged into?
So the worst that can happen is?
If it's a genuine Apple charger, then the worst that can happen is a small tingle. It's part of the way they are designed, with a class Y capacitor between the AC and DC sides. That can leak a tiny current across.
If it's a cheap charger of unknown origin, then the best place for it is the electronics recycling bin.
AJJewsbury:I'm still slightly lost as to what the actual question is. A single USB charger shouldn't draw more than about 15W (0.065A) under any circumstances. But you seem to be asking what will protect against some massive power surge, under some unspecified conditions.
It'll draw an awful lot more than 0.065A if it suffers from an internal short circuit. No power surge required.
- Andy.
I think it's inherent in the design of a wall-wart that you can never get a dead short between the live and neutral pins.
The worst case that I can think of is where a diode in the bridge rectifier fails shorted. In that case, you might get another diode in the rectifier and the EMI filter, suddenly seeing the mains voltage across them. One or both would go "pop" rather violently.
So long as that "pop" is contained by the case, it's fine. They aren't designed to be repairable, so if that happened, you'd throw it away and buy a new one.
Simon Barker:Sparkingchip:Sparkingchip:
What sort of question is that to ask of a guy with a lightning charger lead dangling over the arm of the settee immediately next to him?
Being an Ipad lightning lead the terminals are exposed to touch and every so often I feel a tingle when I put by bare elbow on it, guess what it is plugged into?
So the worst that can happen is?If it's a genuine Apple charger, then the worst that can happen is a small tingle. It's part of the way they are designed, with a class Y capacitor between the AC and DC sides. That can leak a tiny current across.
If it's a cheap charger of unknown origin, then the best place for it is the electronics recycling bin.
Interesting ... does that align with the Ethernet standard ... particularly if the device is connected to a wired connection.
I really worry about devices that are connected to Class II power supplies on the mains side, and then connected via conductive cabling to other devices. Far happier with my laptop with a PELV (functionally earthed) secondary.
HOWEVER this is NOT the case for BS1361, BS88, or BS 3036 rewireable fuses, with BS 3036 being perhaps the worst-case let-through.
AJJewsbury:HOWEVER this is NOT the case for BS1361, BS88, or BS 3036 rewireable fuses, with BS 3036 being perhaps the worst-case let-through.
Interesting. Do you have numbers for BS 3036 fuses? (I (or rather Google) have failed to locate any so far).
Given that the permitted Zs values for a rewireable are if anything a little higher than for either a BS88-3 (e.g. according to table 41.2) I would have though BS 3036 ones would have if anything slightly quicker disconnection times for the same current than an BS 88-3 and therefore (broadly) a lower I²t.
- Andy.
Well to see what I'm saying, have a look at Tables in 3A1 and 3A2, for disconnection times < 0.4 s ... I've put the results, along with the calculated I2t, in the table below:
Fuse |
0.1 s disconnection time |
0.2 s disconnection |
Current |
I2t |
Current |
I2t |
BS 3036 |
450 A |
20,250 A2s |
300 A |
18,000 A2s |
BS 88-3 |
320 A |
10,240 A2s |
280 A |
15,680 A2s |
This is because the curve for the BS 3036 fuses below 1 second compared with the BS 88-3 - so by the time you get to 0.1 s disconnection time, the let-through of a BS 88-3 is half that of the BS 3036.
To see this visually, you could always plot the lines of "maximum disconnection time for current" for a few conductor sizes (say 0.22 through to 25 sq mm) on the graphs ... basically, a 30 A BS 3036 won't protect 1.0 sq mm under any conditions, but a 32 A BS 88-3 will protect 1.0 sq mm for disconnection times of about 0.1 s or less. A 32 A Type B does better again ... provided, of course, the prospective fault current is not too high (because then we'd have to rely on manufacturer's data which would drive up the CSA again.