This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Condition of incoming cable

Hi there, first post on here after losing my old login when the forum migrated!


I have a project where the meter is being moved by western power from in a kitchen to outside in a meter box. As well as relocation to make space in the kitchen the current cut out is leaking pitch (I believe this is because the feed cable comes downhill into the cutout) and needs replacing. Today we have exposed the main cable outside ready for a new piece to be jointed by western power.


The cable was apparently installed back in 1970 and seems in a very poor state (see attached photos), it comes from a pole mounted transformer around 70m away through a wooded area (a slight concern as it doesn't seem to be buried very deep!)


I just wanted some opinions on if it is likely that this cable will have to be replaced in its entirety in the not too distant future, it has a pitch/hessian type wrapping over the armouring (which I believe is the earth and neutral conductor for the installation) and the armouring appears to be quite heavily corroded and breaking down.


I have little experience when it comes to jointing but it seems like it could be a challenge to joint into a cable in this state?


Anyway just looking for some advice in preparation for the arrival of western power,


Thanks in advance,


Will

IMG_9496.JPG

IMG_9495.JPG
Parents
  • I'd say fairly typical of its type/age.  PILC STA was used well into the 70s in some areas for non PME supplies on LV networks.  Sometimes all that is left is the lead sheath (and cores) and a stain in the soil.

    Should joint up just fine though I expect you will get a PME supply for the new location.
Reply
  • I'd say fairly typical of its type/age.  PILC STA was used well into the 70s in some areas for non PME supplies on LV networks.  Sometimes all that is left is the lead sheath (and cores) and a stain in the soil.

    Should joint up just fine though I expect you will get a PME supply for the new location.
Children
No Data