This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Exporting Tnc-s system

Goodmorning all

i have to put power to a wooden shed which is 50 metres away from the house. They will be no services in the shed

I will use SWA cable.

can I export the TNC-S system or I have to make it TT


regards


Paul
Parents
  • Well, I could say with TNC-s you are never sure the potential the CPC will be, relative to earth.  ?

    However, in a self contained equipotential zone, just using the TNC-s Earth will be perfectly fine. As  TT island woudl also be fine as well.

    If it had an earth floor, or was going to supply an  EV charger or a radio shack then TT might be better.

    If using the TNCs earth, please earth the armour at both ends.

    Mike.
Reply
  • Well, I could say with TNC-s you are never sure the potential the CPC will be, relative to earth.  ?

    However, in a self contained equipotential zone, just using the TNC-s Earth will be perfectly fine. As  TT island woudl also be fine as well.

    If it had an earth floor, or was going to supply an  EV charger or a radio shack then TT might be better.

    If using the TNCs earth, please earth the armour at both ends.

    Mike.
Children
No Data