what to do between Consumer unit and trunkin

Former Community Member
Former Community Member
Hello what to use between mains board and trunking when you've made a slot to bring the cables through rather than using bushes. would it be acceptable to leave a slight gap to get  the trunking lid on .
Parents
  • The usual way is to insert a piece of paxolin with a slight small aperture than the board and trunking slot. This provides a gap to get the trunking lid on and also protects the conductor insulation against damage from the metal edges.



    JP
Reply
  • The usual way is to insert a piece of paxolin with a slight small aperture than the board and trunking slot. This provides a gap to get the trunking lid on and also protects the conductor insulation against damage from the metal edges.



    JP