EICR Codes for Consumer unit door not closing

Former Community Member
Former Community Member
I am working on a MK plastic consumer unit and trying to work out if I need to replace it. The problem that concerns me is that the door just covering the fronts of the circuit breakers will not stay closed and remains all the way down or with a 10mm gap at the top.

Looking at the NAPIT EICR code breaker section 4.5 a crack in the access flap would be a C3. There is no indication of how to code a missing or open access flap.

In my mind the risks are dust in the circuit breakers, could also be accidental operation of the circuit breakers(although unlikely in it's current location; I did consider fitting a latch but looks like they are no longer available.


Would appreciate your views on is this a C2 and I need to replace or a C3.


Thanks


Alan
Parents
  • It gets a C3 for being plastic. I cannot find any requirement to have a cover or door in BS EN 61439-3, so no more than that.
Reply
  • It gets a C3 for being plastic. I cannot find any requirement to have a cover or door in BS EN 61439-3, so no more than that.