I can not add a fused connection unit as the box is a double socket box
AJJewsbury:for fusing down extractor fans to 3 Amp for permanent L and 3 Amp for trigger L
Does that make (in BS 7671 terms) two distinct circuits with a shared N?
- Andy.
Dunno about that, but it does follow the manufacturer's instructions about fusing the extractor fan at 3 Amp. This is required if the lighting supply which feeds the light switch triggered timer fan is protected by a 6 or10 Amp M.C.B.
Z.
Zoomup:AJJewsbury:for fusing down extractor fans to 3 Amp for permanent L and 3 Amp for trigger L
Does that make (in BS 7671 terms) two distinct circuits with a shared N?
- Andy.Dunno about that, but it does follow the manufacturer's instructions about fusing the extractor fan at 3 Amp. This is required if the lighting supply which feeds the light switch triggered timer fan is protected by a 6 or10 Amp M.C.B.
Z.
Do the instructions really ask for two separate fuses? I thought the usual solution was to fuse down before the light, so feeding the light and L and SL to the fan with a single fuse. Two fuses with a common N would seem to technically be a contravention of 521.8.2.
- Andy.
Do the instructions really ask for two separate fuses? I thought the usual solution was to fuse down before the light, so feeding the light and L and SL to the fan with a single fuse. Two fuses with a common N would seem to technically be a contravention of 521.8.2.
-
It is not always possible to easily fuse down before a bathroom or shower room light. I thought that your previous question was about to trick me. 521.8.2 does not apply, as I am only dealing with ONE final circuit, that of the lighting circuit feeding a single timer extractor fan. No probs. here.
Z.
OlympusMons:
If the double socket is behind a radiator it might be missed by someone else if the fuse blew.
you could fit an fcu at the light switch with front cable exit (possibly flat plate), then a stand off frame, then the touch controller replacement.
Your 2x3A fuse arrangement might need a 2 sources of supply label in the fan.
The blanked off double socket BOX is behind a small easily removable convector heater. The fuse could be missed but is the lesser of two evils. The circuit can not be overloaded as it only serves two ceiling lights. The fuse would be there to protect from serious faults like rodent damage or nail bashing through cable.
No; F.C.U. with flex outlet that you suggest would not be acceptable to the wife of the house. The single light switch is much neater.
All common timer fans have a Permanent L and a switched trigger L. This is common knowledge. The manufacturers do not supply such a label so obviously consider it unnecessary.
Z.