Wago’s pull test

Hi all.

I've been using wago’s for a couple of years now and more recently the 221 series mainly on lighting circuits. As I do with all terminations, I do a gentle ‘pull test’ after connection which was drummed into me from apprenticeship days to check if the wire is securely held. I also do this with the wago’s but on occasion find that the wire will pull back slightly but not pull out. It can then be pushed forward again fully up into the terminal. I find that this happens more with solid conductors rather than stranded or flex. My query is, am I damaging the internal workings of the wago by carrying out this pull test? I like the reassurance of a pull test on terminations but should it be given a miss on wago’s?


thanks in advance
Parents
  • Chris -

    No, the sockets were not available to fit - Click brushed stainless range and wholesaler was out of them, so I thought I could at least get the testing done. New ring installed by myself a week before so all good. To begin with, I suspected dodgy cable but all was ok once I repeated the tests without the WAGOs. Had a similar problem with r1+ r2 on the new lighting cct too. readings swinging wildly, so much so that I thought my test leads or croc clips were dodgy. I swappped out the WGAO and went old school with a 15A screwed connector and all calmed down. - I use a Fluke 1520 ohm meter with IR range - no all-in-ones for me!
Reply
  • Chris -

    No, the sockets were not available to fit - Click brushed stainless range and wholesaler was out of them, so I thought I could at least get the testing done. New ring installed by myself a week before so all good. To begin with, I suspected dodgy cable but all was ok once I repeated the tests without the WAGOs. Had a similar problem with r1+ r2 on the new lighting cct too. readings swinging wildly, so much so that I thought my test leads or croc clips were dodgy. I swappped out the WGAO and went old school with a 15A screwed connector and all calmed down. - I use a Fluke 1520 ohm meter with IR range - no all-in-ones for me!
Children
No Data