A customer has some underground S.W.A. cable supplying three low level garden lights. The installation is amateurish and now keeps tripping off an R.C.D. He does not want the garden dug up to replace the cable with bad underground joints at the lights. I was wondering if E.L.V. lights could be used at say 12 or 24 Volts via an isolating transformer. Does anyone know of a suitable type of light please? That way the S.W.A could be reused.


Z.
Parents
  • 522.8.10 is obviously aimed at L.V. not E.L.V. The use of the expression "suitable for use as a protective conductor" is a give away..

    I don't think that adds up - you can have protective conductors on ELV - both FELV and PELV - and LV systems without protective conductors are possible too - e.g. separated systems for single items of equipment and fully double/reinforced insulation (a c.p.c. has to be included for the latter in domestic and similar uncontrolled installations of course, but as a general principle it's not required).


    Given the wording and position of 522.8.10 I don't think it can avoided as reading that it should be applied to all systems - if it was intended as applying onto the ADS systems only then section 411 would have been a more obvious location for it for example. Some might think that many of the other provisions (depth, marking tape and so on) would be sensible for any system. I guess they're expecting us to use the conduit/duct option where there isn't a c.p.c. The near-by regulations for cables concealed in walls have an explicit get-out for SELV & PELV circuit - so clearly the 522 section in general is intended to be read as applying to ELV too.


    A while ago in response to one of the DPCs I did suggest an exemption for SELV at least for the earthed sheath/armour bit (and I gather through the grapevine that it was discussed - so the committee are aware that it is being read as applying to SELV/PELV systems) but seem to have decided not to change it.


       - Andy.
Reply
  • 522.8.10 is obviously aimed at L.V. not E.L.V. The use of the expression "suitable for use as a protective conductor" is a give away..

    I don't think that adds up - you can have protective conductors on ELV - both FELV and PELV - and LV systems without protective conductors are possible too - e.g. separated systems for single items of equipment and fully double/reinforced insulation (a c.p.c. has to be included for the latter in domestic and similar uncontrolled installations of course, but as a general principle it's not required).


    Given the wording and position of 522.8.10 I don't think it can avoided as reading that it should be applied to all systems - if it was intended as applying onto the ADS systems only then section 411 would have been a more obvious location for it for example. Some might think that many of the other provisions (depth, marking tape and so on) would be sensible for any system. I guess they're expecting us to use the conduit/duct option where there isn't a c.p.c. The near-by regulations for cables concealed in walls have an explicit get-out for SELV & PELV circuit - so clearly the 522 section in general is intended to be read as applying to ELV too.


    A while ago in response to one of the DPCs I did suggest an exemption for SELV at least for the earthed sheath/armour bit (and I gather through the grapevine that it was discussed - so the committee are aware that it is being read as applying to SELV/PELV systems) but seem to have decided not to change it.