ebee:
This one would niggle me to the "let`s do it right option". re-cable the job or walk away methinks
When passing by the house next I will have a proper look at the planted bollards in the lawn. The customer does not want the lawn dug up to replace the S.W.A. cable. If I can not offer a reliable option I will say so and walk. But the customer may have more work for me of a different kind so I do not want to appear awkward.
Z.
broadgage:
Another option might be to run new ELV cable and abandon the existing.
It is in my view acceptable to install "hi-tuff" or similar at a very shallow depth if it is only for ELV. Gardening operations might damage the cable, but there would be no electrical danger.
Cable may be shallow buried under a lawn without any damage to the lawn. Start at one end of the cable route and drive a spade into the soil. Lever the spade sideways without removing any soil. Poke the cable into the slit, and repeat along the run. Tread the displaced soil back into place.
Not suited for mains voltage, but fine IMHO for ELV at a limited current.
Yes, I have seen that method used to run audio cables from a large mixing desk to a stage in a lawned park for a two day concert. After the concert, the cables are removed, the turves replaced, and nothing seems different. No damage is apparent.
Z.
It is in my view acceptable to install "hi-tuff" or similar at a very shallow depth if it is only for ELV.
AJJewsbury:It is in my view acceptable to install "hi-tuff" or similar at a very shallow depth if it is only for ELV.
522.8.10 would seem to suggest otherwise. It's a bit daft as bell wire inside some flimsy flexible plastic conduit would seem to comply but inherently robust composite cables not. Not clear what protection an earthed metal sheath is meant to provide for an ELV circuit, especially a SELV one, or how to judge 'equivalent protection against mechanical damage' (as distinct from protection from electric shock resulting from mechanical damage).
In any event you've still got the requirements for covers/marking tape and sufficient depth (many lawns get aerated with a garden fork...)
- Andy.
522.8.10 is obviously aimed at L.V. not E.L.V. The use of the expression "suitable for use as a protective conductor" is a give away..
Z.
AJJewsbury:It is in my view acceptable to install "hi-tuff" or similar at a very shallow depth if it is only for ELV.
522.8.10 would seem to suggest otherwise. It's a bit daft as bell wire inside some flimsy flexible plastic conduit would seem to comply but inherently robust composite cables not. Not clear what protection an earthed metal sheath is meant to provide for an ELV circuit, especially a SELV one, or how to judge 'equivalent protection against mechanical damage' (as distinct from protection from electric shock resulting from mechanical damage).
In any event you've still got the requirements for covers/marking tape and sufficient depth (many lawns get aerated with a garden fork...)
- Andy.
I agree that my proposal might not comply with the regulations. In view of the negligible risks, it would however be a reasonable departure.
522.8.10 is obviously aimed at L.V. not E.L.V. The use of the expression "suitable for use as a protective conductor" is a give away..