EICR Basic Insulation on Meter Tails

Former Community Member
Former Community Member
Hi Guys n Girls

Im currenlty doing EICRs for a local authourity.

Basic Insulation od meter tails of more than 15mm showing. So coding it as C2

Client Compliance Manager is saying that I should rectify? But i thought it was ilegal to tamper with DNO equipment? So Im uncomforttable doing this . Compliance manager said he will issue an email stating that it is ok to do this? That also cannot be legal?

What are my options, and where do I stand legally?

Parents
  • Former Community Member
    0 Former Community Member
    G J Ellis:

    I concur with the first two replies.  For my two-penn'th, one of the Housing Associations I worked for had an agreement/"Special Relationship" with the local DNO giving us permission to access and "interfere" with their equipment so that we didn't have to keep calling them out to faults in multiple residences such as the various blocks of flats we owned.  


     


    Indeed, but with so many energy providing companies that can be very difficult to obtain permission from each and every one of them.


Reply
  • Former Community Member
    0 Former Community Member
    G J Ellis:

    I concur with the first two replies.  For my two-penn'th, one of the Housing Associations I worked for had an agreement/"Special Relationship" with the local DNO giving us permission to access and "interfere" with their equipment so that we didn't have to keep calling them out to faults in multiple residences such as the various blocks of flats we owned.  


     


    Indeed, but with so many energy providing companies that can be very difficult to obtain permission from each and every one of them.