Repositioning non fire rated led kitchen spots.

As above,been asked move 6 spots due to new kitchen layout.The ceiling is single boarded with a bedroom above.

Just wondering if all fittings must be changed for fire rated.

                                                                         Regards,Hz

  • City and Guilds Building Regulations for electricians.
  • IET Electricians guide to the Building Regulations.
  • LABC Guide to installing down lights.
  • Or looking at it another way, given that the cans are superior to the open back down lights in every way and are as cheap as chips why are we even having this discussion?
  • Shall we re-ignite the old "inverted terracotta plant pot over tungsten halogen downlighter" debate?
  • Since open backed downlights are still on sale in trade catalogues,,Napits C3( improvement advised) coding if they are installed in a 1st

    floor ceiling of a semi,would render them unusable in most situations if the coding were correct?

                                                                                                                              Regards,

                                                                                                                                       Hz

  • Grumpy:

    Or looking at it another way, given that the cans are superior to the open back down lights in every way and are as cheap as chips why are we even having this discussion?


    The cans caused nothing but problems with the old halogen lamps because of heat build up.  Not too much of a problem with LED.  We are having this discussion because somebody is incorrectly coding them.  



    Gary


  • hertzal123:

    Since open backed downlights are still on sale in trade catalogues,,Napits C3( improvement advised) coding if they are installed in a 1st

    floor ceiling of a semi,would render them unusable in most situations if the coding were correct?

                                                                                                                              Regards,

                                                                                                                                       Hz

                                                            




    Generally they are unusable. 


  • For the cost of 6 fire rated downlighters surely it would be better to replace them?
  • Colin Haggett:

    For the cost of 6 fire rated downlighters surely it would be better to replace them?


    Depends on the customer requirements. If the customer is particularly attached to the exiting ones (fancy or match the ones in the rest of the house or whatever) then we're back to really needing to be sure of our facts.

       - Andy.