Sparkingchip:
Basically it's presenting as a poorly maintained electrical installation and was in need of inspection and testing prior to repair and possibly upgrading.
The schedule of test results indicate the EICR is not fit for purpose.
You have probably wasted your £99 and need to get an electrician in to sort the installation out and prepare another EICR.
Post a picture of the observations and let's see if he had actually explained what the issues are.
It certainly is just a load of rubbish, insulation readings across L and N never told place, r1+r2 for rings are wrong, apparently not a lot was tested. Looks like they just want to make money out of a board change. Then again for £99 what do you expect?
Sparkingchip:
Basically it's presenting as a poorly maintained electrical installation and was in need of inspection and testing prior to repair and possibly upgrading.
The schedule of test results indicate the EICR is not fit for purpose.
You have probably wasted your £99 and need to get an electrician in to sort the installation out and prepare another EICR.
Post a picture of the observations and let's see if he had actually explained what the issues are.
It certainly is just a load of rubbish, insulation readings across L and N never told place, r1+r2 for rings are wrong, apparently not a lot was tested. Looks like they just want to make money out of a board change. Then again for £99 what do you expect?