Can you replace just the RCD, instead of whole consumer unit?

Former Community Member
Former Community Member
My apartment failed it's EICR due to the electrician not being able to trip the RCD in the required time.  I am told that the RCD cannot be replaced and a new metal consumer unit must be installed at a quote of £1180.  The apartment was built in 2003 and seems overly wasteful to ditch the whole unit, however I am not an electrician so would welcome some guidance please before I commit to this remedial action.


This is the RCD currently fitted:
5760S | MK 63 A RCD Switch, Trip Sensitivity 30mA | RS Components (rs-online.com)


It appears it worked within spec for above 30mA, but failed for below, if that helps with whether the whole consumer unit must be replaced.  See report.
Capture2.JPG
Parents
  • I am here.

    That is far from a competent EICR, it is being used to make money as usual. I suggest you write a review of this man pointing out that the EICR is not competent within the meaning of BS7671 and is therefore valueless. Did you agree to all those limitations in the inspection? If not he has not done the job at all! I would demand the £99 back as well because this is a ripoff. I presume the new quote is for a full set of AFDDs too, I'd like to see that for my "black" book pile.
Reply
  • I am here.

    That is far from a competent EICR, it is being used to make money as usual. I suggest you write a review of this man pointing out that the EICR is not competent within the meaning of BS7671 and is therefore valueless. Did you agree to all those limitations in the inspection? If not he has not done the job at all! I would demand the £99 back as well because this is a ripoff. I presume the new quote is for a full set of AFDDs too, I'd like to see that for my "black" book pile.