This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Can you replace just the RCD, instead of whole consumer unit?

Former Community Member
Former Community Member
My apartment failed it's EICR due to the electrician not being able to trip the RCD in the required time.  I am told that the RCD cannot be replaced and a new metal consumer unit must be installed at a quote of £1180.  The apartment was built in 2003 and seems overly wasteful to ditch the whole unit, however I am not an electrician so would welcome some guidance please before I commit to this remedial action.


This is the RCD currently fitted:
5760S | MK 63 A RCD Switch, Trip Sensitivity 30mA | RS Components (rs-online.com)


It appears it worked within spec for above 30mA, but failed for below, if that helps with whether the whole consumer unit must be replaced.  See report.
Capture2.JPG
Parents
  • Or to put it another way, an electrician doing an EICR should never find a consumer unit in that condition, it is only like that because of other people’s failings.
Reply
  • Or to put it another way, an electrician doing an EICR should never find a consumer unit in that condition, it is only like that because of other people’s failings.
Children
No Data