Chris Pearson:LB2:
I have spoken with another electrician to get a second opinion, he said that the test results seem strange, as the trip responded in 30ms above 30mA as it should, but marked faulty because it didn't trip below 30mA but electrician 2 seems to think that's by design and shouldn't trip with currents lower than 30mA.
I took this to mean that if the RCD is a 30 mA one (or 10 mA) it is tested at 5 times the value, but if it is > 30 mA (100 mA, 300 mA, etc.) it is tested at 1 times the value.
It need not trip below 30 mA, but should do so rapidly at 150 mA. On the face of it, it has not tripped at all.
Interesting, many thanks. Apologies if I'm missing something, but as there is only one RCD, shouldn't only one of those boxes be filled? ie there's one '30mA or below' RCD so the 'Above 30mA' shouldn't have a value in it?
Chris Pearson:LB2:
The RCD is separate to the main switch, I now have photographs. I was mistaken in the RCD type, it is infact an MK Sentry 5760sAs far as I can see, the product has been discontinued, but there do seem to be some around.
When looking for replacements, would it matter if I found one from the same MK series with a higher amperage - 80A or 100A?
mapj1:
To test an RCD fully involves more tests at different fault currents.
I presume it always fires smartly on the test button like you test it every few months... (yeah right...)
For that model it should always trip at 30mA or above. and may trip at faults between 15mA and 30mA
and should never trip below 15mA.
It is common to test at 30mA and 150mA, and perhaps 15mA as well.
That is not an IET standard form, but is presumably created by some testing sofware, and has most but not all of the same stuff.
It does look like a discontinued model, but there seem to be a few places still with stock, so if that is the only issue it may well be worth tracking one down.
One from the same family but say the 80A one should fit just as well - inside the contacts are a bit boskier.
Mike.
I phoned MK who advised that either another 5760s or the more readily available 7860s are identical and interchangeable so I will find a new unit for my electrician. Many thanks
LB2:
My apartment failed it's EICR due to the electrician not being able to trip the RCD in the required time.
I would recommend a second opinion - get a retest of the RCD.with a proven, calibrated instrument and get a quote for a replacement R.C.D ...... if needed.