Sparkingchip:
I assume that the socket circuits have been taken off the RCD side of the consumer unit leaving all the circuits without any RCD protection, rather than sorting out the problems within the installation.
I see what you mean. RCD was originally 18 mm to the left with the two MCBs to the right of it. Now there is nothing on the load side of the MCB, so plugging in tester to a socket definitely isn't going to trip it in a month of Sundays. So we have I&T with no inspection in the CU!
DZ, where are you?
Sparkingchip:
Basically it's presenting as a poorly maintained electrical installation and was in need of inspection and testing prior to repair and possibly upgrading.
The schedule of test results indicate the EICR is not fit for purpose.
You have probably wasted your £99 and need to get an electrician in to sort the installation out and prepare another EICR.
Post a picture of the observations and let's see if he had actually explained what the issues are.
It certainly is just a load of rubbish, insulation readings across L and N never told place, r1+r2 for rings are wrong, apparently not a lot was tested. Looks like they just want to make money out of a board change. Then again for £99 what do you expect?