This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

2 x 1ph cables used as 3ph...

Ok probably stupid question

I'm pretty sure this cant be done .. 


We have 2 x 35mm 1ph armoureds feeding a building..

the cables run through ducting next to each other.


The building is to be modified and requires 1 x 3ph supply...


Is it against regs to use one cable as  L1 , N , E

And the second cable as  L2, L3, E         Or     L2, L3, N




Parents Reply Children
No Data