Caravan hook up

Former Community Member
Former Community Member
Hi I am fitting a caravan hook up on the wall next to  the dno incomer box. No wires exposed. Do I still require an earth rod. The earth bond will be prob 1 ft long inside so not exposed. I know if I fit the box away using swa then yes earth rod would be used.
Parents
  • as the risk of loose of earth would be very reduced as its so short

    The issue isn't the risk of a break in the PE/c.p.c. between the intake and the caravan (that wouldn't immediately produce danger unless there was a simultanous L-PE fault in the caravan or there was high earth leakage equipment installed) - the worry is a break in the distribution network's combined neutral & earth (CNE or PEN) conductor. If that happens it would not only mean the loss of earth, but as there's almost certainly some loads connected, the severed neutral/CNE would be immediately pulled up to something approaching full mains voltage - and as the installation's earthing system is connected directly to the CNE under the PME system a single fault can cause all earthed metalwork to be very hazardous live - and for an indefinite period (i.e. until someone notices, calls the DNO and they send someone out in a van to fix it). That's not too bad inside a building where everything should be bonded together anyway, but outside where someone is likely to be in contact with the general mass of the earth, it's a different story.


    That's why it's only an issue with PME (TN-C-S systems) - true TN-S systems don't have the same immediate hazard.


       - Andy.
Reply
  • as the risk of loose of earth would be very reduced as its so short

    The issue isn't the risk of a break in the PE/c.p.c. between the intake and the caravan (that wouldn't immediately produce danger unless there was a simultanous L-PE fault in the caravan or there was high earth leakage equipment installed) - the worry is a break in the distribution network's combined neutral & earth (CNE or PEN) conductor. If that happens it would not only mean the loss of earth, but as there's almost certainly some loads connected, the severed neutral/CNE would be immediately pulled up to something approaching full mains voltage - and as the installation's earthing system is connected directly to the CNE under the PME system a single fault can cause all earthed metalwork to be very hazardous live - and for an indefinite period (i.e. until someone notices, calls the DNO and they send someone out in a van to fix it). That's not too bad inside a building where everything should be bonded together anyway, but outside where someone is likely to be in contact with the general mass of the earth, it's a different story.


    That's why it's only an issue with PME (TN-C-S systems) - true TN-S systems don't have the same immediate hazard.


       - Andy.