Sparkingchip:gkenyon:.
In truth, caravans should not be plugged in at homes with PME earthing arrangements.
From my front window I can see a motor home plugged into an extension lead running from within a house, it’s connected to a PME supply, via a Type AC 30 mA RCD in the consumer unit. I know that because I fitted the consumer unit around ten years ago, long before the neighbours bought the motor home.
A socket is a socket, what’s the issue? Why would a caravan or motor home user question plugging it into any electric socket?
I agree they wouldn't ... but it's still the DNO's responsibility, under Regulation 9(4) of ESQCR, to ensure this doesn't happen ... and not a "so far as reasonably practicable" legal requirement either:
(4) The distributor shall not connect his combined neutral and protective conductor to any metalwork in a caravan or boat.
Sparkingchip:gkenyon:.
In truth, caravans should not be plugged in at homes with PME earthing arrangements.
From my front window I can see a motor home plugged into an extension lead running from within a house, it’s connected to a PME supply, via a Type AC 30 mA RCD in the consumer unit. I know that because I fitted the consumer unit around ten years ago, long before the neighbours bought the motor home.
A socket is a socket, what’s the issue? Why would a caravan or motor home user question plugging it into any electric socket?
I agree they wouldn't ... but it's still the DNO's responsibility, under Regulation 9(4) of ESQCR, to ensure this doesn't happen ... and not a "so far as reasonably practicable" legal requirement either:
(4) The distributor shall not connect his combined neutral and protective conductor to any metalwork in a caravan or boat.