Caravan hook up

Former Community Member
Former Community Member
Hi I am fitting a caravan hook up on the wall next to  the dno incomer box. No wires exposed. Do I still require an earth rod. The earth bond will be prob 1 ft long inside so not exposed. I know if I fit the box away using swa then yes earth rod would be used.
Parents
  • Sparkingchip:
    gkenyon:.



    In truth, caravans should not be plugged in at homes with PME earthing arrangements.






    From my front window I can see a motor home plugged into an extension lead running from within a house, it’s connected to a PME supply, via a Type AC 30 mA RCD in the consumer unit. I know that because I fitted the consumer unit around ten years ago, long before the neighbours bought the motor home.


    A socket is a socket, what’s the issue? Why would a caravan or motor home user question plugging it into any electric socket?




    I agree they wouldn't ... but it's still the DNO's responsibility, under Regulation 9(4) of ESQCR, to ensure this doesn't happen ... and not a "so far as reasonably practicable" legal requirement either:



    (4) The distributor shall not connect his combined neutral and protective conductor to any metalwork in a caravan or boat.


    And I have to also agree ... why is an EV different to a motor home different to a caravan etc?


    Although, a caravan in a field is a very different situation to a caravan on an urban driveway.
Reply
  • Sparkingchip:
    gkenyon:.



    In truth, caravans should not be plugged in at homes with PME earthing arrangements.






    From my front window I can see a motor home plugged into an extension lead running from within a house, it’s connected to a PME supply, via a Type AC 30 mA RCD in the consumer unit. I know that because I fitted the consumer unit around ten years ago, long before the neighbours bought the motor home.


    A socket is a socket, what’s the issue? Why would a caravan or motor home user question plugging it into any electric socket?




    I agree they wouldn't ... but it's still the DNO's responsibility, under Regulation 9(4) of ESQCR, to ensure this doesn't happen ... and not a "so far as reasonably practicable" legal requirement either:



    (4) The distributor shall not connect his combined neutral and protective conductor to any metalwork in a caravan or boat.


    And I have to also agree ... why is an EV different to a motor home different to a caravan etc?


    Although, a caravan in a field is a very different situation to a caravan on an urban driveway.