Former Community Member
Former Community Member
Hi I am fitting a caravan hook up on the wall next to  the dno incomer box. No wires exposed. Do I still require an earth rod. The earth bond will be prob 1 ft long inside so not exposed. I know if I fit the box away using swa then yes earth rod would be used.
Parents
  • In what way is this suggestion different from hundreds of items of street furniture?

    Possibly it's somewhat more likely that someone will take a firm grip of a caravan door handle/frame while entering/exiting (probably many times and hour if loading/unloading) - I suspect the numbers for touching the local lamppost would be somewhat lower.


    Also the additional electrodes for street lighting are likely to be reasonably effective given the small loads - a caravan hooked up to a 100A domestic PME supply won't have that luxury.


       - Andy.
Reply
  • In what way is this suggestion different from hundreds of items of street furniture?

    Possibly it's somewhat more likely that someone will take a firm grip of a caravan door handle/frame while entering/exiting (probably many times and hour if loading/unloading) - I suspect the numbers for touching the local lamppost would be somewhat lower.


    Also the additional electrodes for street lighting are likely to be reasonably effective given the small loads - a caravan hooked up to a 100A domestic PME supply won't have that luxury.


       - Andy.