Caravan hook up

Former Community Member
Former Community Member
Hi I am fitting a caravan hook up on the wall next to  the dno incomer box. No wires exposed. Do I still require an earth rod. The earth bond will be prob 1 ft long inside so not exposed. I know if I fit the box away using swa then yes earth rod would be used.
  • Former Community Member
    0 Former Community Member
    Like EV chargers technology could change the regs on this subject as they changed the EV charger instalation due to its demand and promoting a cleaner earth as in planet.
  • If you have a look for caravan electrical equipment and cables on the internet you will soon realise hardly anything on offer actually complies with the requirements of the Wiring Regulations BS7671.

    Or indeed BS 7671 doesn't comply with accepted good practice in the caravanning sector - the vast majority of electric hook-up leads are bright orange - so they can be seen clearly against the grass and so greatly reduce the chances of trips or being mowed over ... yet BS 7671 demands rubber types (H05RN-F or H07RN-F or equivalent) which as far as I can tell are only available in matt black.


    And as for attempting to apply the general requirements of BS 7671 on top of A721 for the 12V system is a complete non-starter.


       - Andy.
  • Chris Pearson:
    Sparkingchip:

    Interesting combination.

    https://www.ebay.co.uk/itm/154016689192


    Yes, I am struggling with the idea of a socket at both ends. It looks good, but I am also having difficulty identifying the member on the NICEIC site.






    I have seen the 16 amp plugs and sockets reversed, on one occasion it was on the supply cable to a hired inflatable bouncy castle at a children's birthday party in a private garden.


  • AJJewsbury:
    If you have a look for caravan electrical equipment and cables on the internet you will soon realise hardly anything on offer actually complies with the requirements of the Wiring Regulations BS7671.

    Or indeed BS 7671 doesn't comply with accepted good practice in the caravanning sector - the vast majority of electric hook-up leads are bright orange - so they can be seen clearly against the grass and so greatly reduce the chances of trips or being mowed over ... yet BS 7671 demands rubber types (H05RN-F or H07RN-F or equivalent) which as far as I can tell are only available in matt black.


    And as for attempting to apply the general requirements of BS 7671 on top of A721 for the 12V system is a complete non-starter.


       - Andy.





    That is an interesting regulation that may be worthy of discussion, due to what Eland Cables say on their website:


    The H05RN-F cable is the 300/500V variant of the H07RN-F 450/750V cable, with Class 5 flexible copper conductor cross-sectional area sizes of 0.75mm2 and 1mm2 only.
    H05RN-F Cable | Eland Cables


    So, how can H05RN-F cable meet the requirements stated in The Wiring Regulations BS7671 for a caravan hook up lead to have a minimum conductor size of 2.5mm?


  • Chris Pearson:
    Sparkingchip:

    Interesting combination.

    https://www.ebay.co.uk/itm/154016689192


    Yes, I am struggling with the idea of a socket at both ends. It looks good, but I am also having difficulty identifying the member on the NICEIC site.




    Member is ACC Electrical in Folkestone, registered with NICEIC as approved contractors and domestic installers


  • AJJewsbury:
    If you have a look for caravan electrical equipment and cables on the internet you will soon realise hardly anything on offer actually complies with the requirements of the Wiring Regulations BS7671.

    Or indeed BS 7671 doesn't comply with accepted good practice in the caravanning sector - the vast majority of electric hook-up leads are bright orange - so they can be seen clearly against the grass and so greatly reduce the chances of trips or being mowed over ... yet BS 7671 demands rubber types (H05RN-F or H07RN-F or equivalent) which as far as I can tell are only available in matt black.


    And as for attempting to apply the general requirements of BS 7671 on top of A721 for the 12V system is a complete non-starter.


       - Andy.


    PVC cables are not suitable for being left in standing water ...


    So I wouldn't necessarily say that it's BS 7671 not complying with good practice - and also consider that we are talking about the implementation of an HD here. So, an assembled product complying with LVD should comply with relevant ENs and HDs unless the manufacturer self-certifies otherwise ?


    Agree on visibility, and also would like to point out there's a huge price difference between H0xRN-F and H0xVV-F.


  • There are people advertising Bulgin connectors for connecting caravan and motor home connection leads, how do those rate for suitability?

    https://www.ebay.co.uk/itm/202942721192


    There is a note that they need to be sealed with superglue.


  • And note the standards referenced ?
  • Whilst on standards, is Flame propagation to BS EN 50265 the same as meeting the requirements of BS EN 60332-1-2 ?
  • I was just wondering Gino, do you possess a boat?


    Regards, UKPNZap