Cable grouping factors



Note 1 of table 4C1 in Apdx 4, says that the factors are applicable to uniform groups of cables, equally loaded. However, I see some publications that apply these factors to ccts, in trunking, for example, with no reference to cables being equally loaded (as though it's a belt-and-braces approach and apply the factors regardless). 


So what is your interpretation of equally loaded? It could apply to cables in conduit or trunking supplying heaters or conveyor belt motors, for example, all on for long durations. But what of cables supplying e.g. ring f. ccts, an EVC and other ccts, such as in domestic settings? Can they basically be ignored from such grouping factors or apply them regardless just to be in the safe side?


Parents
  • Farmboy:


    Note 1 of table 4C1 in Apdx 4, says that the factors are applicable to uniform groups of cables, equally loaded. However, I see some publications that apply these factors to ccts, in trunking, for example, with no reference to cables being equally loaded (as though it's a belt-and-braces approach and apply the factors regardless). 


    So what is your interpretation of equally loaded? It could apply to cables in conduit or trunking supplying heaters or conveyor belt motors, for example, all on for long durations. But what of cables supplying e.g. ring f. ccts, an EVC and other ccts, such as in domestic settings? Can they basically be ignored from such grouping factors or apply them regardless just to be in the safe side?

     


    Equally loaded just means that that's what they've assumed when calculating the numbers in that table (i.e. every cable is carry the same and as much as it can without anything overheating). Trying to create tables for other conditions rapidly gets very silly as there are just too many combinations of how things could be arranged (90% fully loaded, 10% half loaded; 50% full loaded, 25% half loaded, 10% 10% loaded 15% unloaded....)


    Where things aren't equally loaded then it's NOT saying you can ignore grouping - it's just saying that the figures in that particular table might not be entirely accurate - hinting that you might need to take other factors into consideration (i.e. apply some engineering judgement). As you say for other cases the tabulated values are likely to be erring on the safe side, so applying them directly if you don't really know much more about the loads probably isn't a bad approach. But where you do know something about the nature of the load .. or indeed any upstream overload protection ... you can often justify some significantly more favourable numbers.


    In practice, for domestic socket and lighting loads, grouping factors are often ignored - but care is still needed especially for large long-duration loads (traditionally immersion heaters and night storage heaters).


       - Andy.


Reply
  • Farmboy:


    Note 1 of table 4C1 in Apdx 4, says that the factors are applicable to uniform groups of cables, equally loaded. However, I see some publications that apply these factors to ccts, in trunking, for example, with no reference to cables being equally loaded (as though it's a belt-and-braces approach and apply the factors regardless). 


    So what is your interpretation of equally loaded? It could apply to cables in conduit or trunking supplying heaters or conveyor belt motors, for example, all on for long durations. But what of cables supplying e.g. ring f. ccts, an EVC and other ccts, such as in domestic settings? Can they basically be ignored from such grouping factors or apply them regardless just to be in the safe side?

     


    Equally loaded just means that that's what they've assumed when calculating the numbers in that table (i.e. every cable is carry the same and as much as it can without anything overheating). Trying to create tables for other conditions rapidly gets very silly as there are just too many combinations of how things could be arranged (90% fully loaded, 10% half loaded; 50% full loaded, 25% half loaded, 10% 10% loaded 15% unloaded....)


    Where things aren't equally loaded then it's NOT saying you can ignore grouping - it's just saying that the figures in that particular table might not be entirely accurate - hinting that you might need to take other factors into consideration (i.e. apply some engineering judgement). As you say for other cases the tabulated values are likely to be erring on the safe side, so applying them directly if you don't really know much more about the loads probably isn't a bad approach. But where you do know something about the nature of the load .. or indeed any upstream overload protection ... you can often justify some significantly more favourable numbers.


    In practice, for domestic socket and lighting loads, grouping factors are often ignored - but care is still needed especially for large long-duration loads (traditionally immersion heaters and night storage heaters).


       - Andy.