Chris Pearson:
Where I think that this concept fails is in ring circuits. By definition only one circuit, but imagine a circuit high up in conduit: down and up, over a door, down and up again, etc; or domestic under the floorboards, down and up (or up and down) under the capping, down and up again, etc. If the main load is half way round, that's the whole lot in two adjacent cables. Should that not be treated as two circuits?
I asked the nic about that, some time ago, and they said that for domestics they read it as for ccts, so wouldn't be concerned about individual legs if the ring was generally lightly loaded most of the time. However, for comm/ind they would apply the group ratings to the legs, depending on anticipated use/load. Others, of course, may disagree.
Chris Pearson:
Where I think that this concept fails is in ring circuits. By definition only one circuit, but imagine a circuit high up in conduit: down and up, over a door, down and up again, etc; or domestic under the floorboards, down and up (or up and down) under the capping, down and up again, etc. If the main load is half way round, that's the whole lot in two adjacent cables. Should that not be treated as two circuits?
I asked the nic about that, some time ago, and they said that for domestics they read it as for ccts, so wouldn't be concerned about individual legs if the ring was generally lightly loaded most of the time. However, for comm/ind they would apply the group ratings to the legs, depending on anticipated use/load. Others, of course, may disagree.