Cable grouping factors



Note 1 of table 4C1 in Apdx 4, says that the factors are applicable to uniform groups of cables, equally loaded. However, I see some publications that apply these factors to ccts, in trunking, for example, with no reference to cables being equally loaded (as though it's a belt-and-braces approach and apply the factors regardless). 


So what is your interpretation of equally loaded? It could apply to cables in conduit or trunking supplying heaters or conveyor belt motors, for example, all on for long durations. But what of cables supplying e.g. ring f. ccts, an EVC and other ccts, such as in domestic settings? Can they basically be ignored from such grouping factors or apply them regardless just to be in the safe side?


Parents
  • Farmboy:


    ...

    presumably then each leg should also be run separately in floor joists - at the risk of making Swiss cheese out of the joists with all the cables run in separate holes, or upping the cable size based on rating factors.

    ...




     Extra holes not really required unless the parallel length of touching cables in the joist was so long that no significant heat conducted along the cable, and the fit so tight that no air could move between them - so perhaps a very thick joist like a ship's timber, but not the average bit of 2*8 or 3*10 - (even less  of a concern in the 'engineered joists' that are an I beam of 2 bits of what looks like roof batten attached to a strip of plywood)

    If in doubt a slight slotting in the direction of the grain is enough to open up an air path, though to be honest T &E being flat, in a round hole, I'd not worry.

    Because the heat generated (and in the simple systems the temperature rise ) is proportional to the square of current you  may find do not need to de-rate so much - 70% of the current in 2 cables is the same total heating as 100% of the heat in one cable (as 1.4 is sqrt of 2), but of course the surface area to sweat it out over is increased over the single cable case (but not quite doubled as the sides in contact are unable to lose heat in the way they would be if there was a gap between the cables) Also flat cables touching on the thin edge cool better than touching on the broadside - but this sort of thing rapidly becomes subject to too many subtle effects to be safely captured in a simple set of rules.

    However a round bundle of cables is the worst case, for the one in the middle, and keeps getting worse the more cables are added, while if you can lay your cables  side by side, then only the nearest few neighbours to any given cable have much effect, and the effect on the grouping factor is that for more than a few cables the change in cg of adding another cable is small - the greatest steps are between 1 and 2 and then 2 and 3 cables, and a flat lay of 4 cables is almost the same as a flat lay of 40.

    Mike


    regards,

    Mike.


Reply
  • Farmboy:


    ...

    presumably then each leg should also be run separately in floor joists - at the risk of making Swiss cheese out of the joists with all the cables run in separate holes, or upping the cable size based on rating factors.

    ...




     Extra holes not really required unless the parallel length of touching cables in the joist was so long that no significant heat conducted along the cable, and the fit so tight that no air could move between them - so perhaps a very thick joist like a ship's timber, but not the average bit of 2*8 or 3*10 - (even less  of a concern in the 'engineered joists' that are an I beam of 2 bits of what looks like roof batten attached to a strip of plywood)

    If in doubt a slight slotting in the direction of the grain is enough to open up an air path, though to be honest T &E being flat, in a round hole, I'd not worry.

    Because the heat generated (and in the simple systems the temperature rise ) is proportional to the square of current you  may find do not need to de-rate so much - 70% of the current in 2 cables is the same total heating as 100% of the heat in one cable (as 1.4 is sqrt of 2), but of course the surface area to sweat it out over is increased over the single cable case (but not quite doubled as the sides in contact are unable to lose heat in the way they would be if there was a gap between the cables) Also flat cables touching on the thin edge cool better than touching on the broadside - but this sort of thing rapidly becomes subject to too many subtle effects to be safely captured in a simple set of rules.

    However a round bundle of cables is the worst case, for the one in the middle, and keeps getting worse the more cables are added, while if you can lay your cables  side by side, then only the nearest few neighbours to any given cable have much effect, and the effect on the grouping factor is that for more than a few cables the change in cg of adding another cable is small - the greatest steps are between 1 and 2 and then 2 and 3 cables, and a flat lay of 4 cables is almost the same as a flat lay of 40.

    Mike


    regards,

    Mike.