Zoomup:consider the need to instant trip a C type 63A unit - if it does not trip the rest of the morning may be lost to getting the company fuse changed.
A rare beast in the domestic world I feel. And even in shops and offices.
Z.
Possibly a C63 is an extreme example (but not unknown for say submains to remote CUs) - but even a relatively common B50 would need 250A to test for instantaneous operation - which won't to the DNO's fuse much good if it persists for long.
- Andy.
Zoomup:consider the need to instant trip a C type 63A unit - if it does not trip the rest of the morning may be lost to getting the company fuse changed.
A rare beast in the domestic world I feel. And even in shops and offices.
Z.
Possibly a C63 is an extreme example (but not unknown for say submains to remote CUs) - but even a relatively common B50 would need 250A to test for instantaneous operation - which won't to the DNO's fuse much good if it persists for long.
- Andy.