The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement

This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Reference Methods

Former Community Member
Former Community Member
Wondered what installation reference method people might be using for a T&E cable on a masonry wall that is then covered with plasterboard, ie a typical dot and dab affair. I think "C" is correct as all installation methods involving a cable in contact with a wall and NO insulation map to reference method "C". Wouldn't think the plasterboard or covering the cable with capping would make any difference. I raised the question due to seeing A,B, & C on various other contractors certs.
Parents
  • Covered in insulation, whether in containment or not = "A"

    Excepting that for T&E you'd probably be looking at methods 100 - 103.

      - Andy.
Reply
  • Covered in insulation, whether in containment or not = "A"

    Excepting that for T&E you'd probably be looking at methods 100 - 103.

      - Andy.
Children
No Data