Reference Methods

Former Community Member
Former Community Member
Wondered what installation reference method people might be using for a T&E cable on a masonry wall that is then covered with plasterboard, ie a typical dot and dab affair. I think "C" is correct as all installation methods involving a cable in contact with a wall and NO insulation map to reference method "C". Wouldn't think the plasterboard or covering the cable with capping would make any difference. I raised the question due to seeing A,B, & C on various other contractors certs.
Parents
  • Geez:

    Gary,

    These are not actually domestics, the walls form the common stairwell in a block of flats so the end of the circuit is just the top light fitting.


    I personally think reference methods are an easy source of confusion, there are common installation methods that are not specifically mentioned in the BS. Looking at all the methods I can deduce the following:


    Covered in insulation, whether in containment or not = "A"

    Cable inside containment, no insulation = "B"

    Cable touching, or very close to a wall = "C"


    Tom, my apologies, I hijacked the thread a bit. ? Cables are found in masonry all over the place - domestics, the smarter common areas, the public side of hotels, etc.) and I have no doubt that "C" is correct and I agree with your rule of thumb.


    In the example that I described, I went for 100# to be on the safe side. I don't know what was stuffed in the ceilings after I left. The only potential bugbear would be that 4 mm² would no longer do for a radial on a 32 A breaker.


    I also agree concerning EIC as opposed to EICR - difficult to know exactly what is below (or above) the surface. Of course when you come to do an EICR, you will be presented with a folder containing the EIC and any previous EICRs will you not? ?


Reply
  • Geez:

    Gary,

    These are not actually domestics, the walls form the common stairwell in a block of flats so the end of the circuit is just the top light fitting.


    I personally think reference methods are an easy source of confusion, there are common installation methods that are not specifically mentioned in the BS. Looking at all the methods I can deduce the following:


    Covered in insulation, whether in containment or not = "A"

    Cable inside containment, no insulation = "B"

    Cable touching, or very close to a wall = "C"


    Tom, my apologies, I hijacked the thread a bit. ? Cables are found in masonry all over the place - domestics, the smarter common areas, the public side of hotels, etc.) and I have no doubt that "C" is correct and I agree with your rule of thumb.


    In the example that I described, I went for 100# to be on the safe side. I don't know what was stuffed in the ceilings after I left. The only potential bugbear would be that 4 mm² would no longer do for a radial on a 32 A breaker.


    I also agree concerning EIC as opposed to EICR - difficult to know exactly what is below (or above) the surface. Of course when you come to do an EICR, you will be presented with a folder containing the EIC and any previous EICRs will you not? ?