Generator earthing

Hi


I have a tractor driven Backup generator to install on a farm shortly and have a query regarding the earth spike. Does it need to go directly back to the MET or can I connect it directly into the generator earth terminal, the latter being Quite a lot simpler   In my case? 


thanks

Parents
  • If more than 3kW then BS 7430 says you need an independent earth electrode for the generator with an earth resistance of 20 ohms or less.