Coordination of insulation monitoring devices

Hi all,


I occaisionally come up againt a requirement to provide an IMD where there already is one elsewhere on the same network (for example, on an IT system where the downstream equipment contains its own IMD out of the box, but has been installed in such a way that it might be disconnected with the distribution circuits still energised, leaving the latter unprotected)


In the past I've been advised by manufacturers that you can't have two separate IMDs monitoring the same network as they'll see each other as faults, so we've ended up with convoluted arrangements to priorise devices such that only one is in use at any time, or simply removed downstream devices.


But this doesn't feel satisfactory to me, and I suspect I'm missing something... Is there a better way to coordinate IMDs?
Parents
  • Not that unusual to me: Large inverters (>500kWish) are almost invariably arranged IT and fed from a dedicated transformer. I believe the reason is to minimise hazard to personnel and risk of fire in the event of first fault, since sites are normally unmanned in a stressful environment, plus the international market they sell and customer preferene to avoid downtime (although I've never actually had a straight answer from a manufacturer).


    Anyway, the feeling seems to be, as I first thought, that it's not possible to have multiple IMDs, and that where it appears necessary the answer is to either ensure that only one is "live" at any time (in some fail-safe manner) or to re-arrange things so it's not required.


    Thanks for your thoughts.
Reply
  • Not that unusual to me: Large inverters (>500kWish) are almost invariably arranged IT and fed from a dedicated transformer. I believe the reason is to minimise hazard to personnel and risk of fire in the event of first fault, since sites are normally unmanned in a stressful environment, plus the international market they sell and customer preferene to avoid downtime (although I've never actually had a straight answer from a manufacturer).


    Anyway, the feeling seems to be, as I first thought, that it's not possible to have multiple IMDs, and that where it appears necessary the answer is to either ensure that only one is "live" at any time (in some fail-safe manner) or to re-arrange things so it's not required.


    Thanks for your thoughts.