R1+R2 on 2 core Hi Tuff

Former Community Member
Former Community Member
Hi all,


At a property yesterday that has a garage submain being fed from the main house CU in 2.5mm 2 core Hi Tuff fed in conduit underground. The main installation is TNCS and the garage CU is TT from a stake just outside the door. When reporting test results on the main CU, how would you record an R1+R2 value?


Very rarely do I come across TT so any help is, well, helpful!
Parents
  • You could not (R2) is the cpc value, and you do not have one. R1+R2 is to establish 1.Earth continuity 2. Calculate Zs if required.


    Colin
Reply
  • You could not (R2) is the cpc value, and you do not have one. R1+R2 is to establish 1.Earth continuity 2. Calculate Zs if required.


    Colin