ATEX equipment and gland hole drilling

Former Community Member
Former Community Member
i have specified a number of hawke PL630 JBs for a project i am working on, i was under the impression that these could be drilled by the installer as required (providing that the quantity and diameter of holes per face is in accordance with manufacturers reccomendations), however, having spoken to hawke i have been advised that these have to be drilled by a certified company.


just wondering if anybody had some good information on the requirements for self certification, and what equipment can/cant be drilled on site, as i obviously have been mislead into what i thought was accurate and correct knowledge. 


my impression was that anything that wasnt Exd flameproof could be drilled by anybody so long as it was in accordance with manufacturers information.
Parents
  • Roger Bryant:

    The Hawke documentation states:

    ----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------

    b) The enclosure may be ready supplied with cable entries. Where the customer drills cable entries they must be installed in accordance with

    the component certificate BAS06ATEX0116U or IEC Ex No: BAS06.0027U and enclosure limitations, these specify a maximum clearance on

    the entry thread of 0.7mm for plain holes and where adjacent cable entries are installed suficient clearance must be maintained to allow

    for the fitting of sealing/retaining washers and the rotation of the cable gland hexagons, and leave a minimum of material between

    adjacent holes in line with the above certificate number(s).

    --------------------------------------------------------------------------------------------------------------------------------------------------------------------------------

    https://hubbellcdn.com/installationmanuals/HKE_AI273 PL6 Junction Box (Issue Y 03-19).pdf


    As I read this you would have to be able to make the hole to the required tolerance -0, +0.7mm and be able to confirm this with a calibrated go -no go gauge. You would also have to demonstrate that you have met the requirements for spacing of adjacent holes in accordance with the stated certificate.


    On a purely practical basis you will not be able to acheive those tolerances with a hand held hole saw. A rigid bench drill or mill with an appropriate cutter will be required.


    Yes, 0.7mm is the typical maximum clearance hole for metric glands (comes from a standard, can't remember which off top of my head)

    When I looked at the documentation for the component certified enclosure ( BAS06ATEX0116U) last night, it doesn't actually give the required information. It refers to another drawing which I didn't see on their website. I wondered if this might be the point where the OP contacted them?

    Then their advice might be correct based on what he told them, or there might have been a misunderstanding.  It all depends on where he lies in the supply chain or end user.


Reply
  • Roger Bryant:

    The Hawke documentation states:

    ----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------

    b) The enclosure may be ready supplied with cable entries. Where the customer drills cable entries they must be installed in accordance with

    the component certificate BAS06ATEX0116U or IEC Ex No: BAS06.0027U and enclosure limitations, these specify a maximum clearance on

    the entry thread of 0.7mm for plain holes and where adjacent cable entries are installed suficient clearance must be maintained to allow

    for the fitting of sealing/retaining washers and the rotation of the cable gland hexagons, and leave a minimum of material between

    adjacent holes in line with the above certificate number(s).

    --------------------------------------------------------------------------------------------------------------------------------------------------------------------------------

    https://hubbellcdn.com/installationmanuals/HKE_AI273 PL6 Junction Box (Issue Y 03-19).pdf


    As I read this you would have to be able to make the hole to the required tolerance -0, +0.7mm and be able to confirm this with a calibrated go -no go gauge. You would also have to demonstrate that you have met the requirements for spacing of adjacent holes in accordance with the stated certificate.


    On a purely practical basis you will not be able to acheive those tolerances with a hand held hole saw. A rigid bench drill or mill with an appropriate cutter will be required.


    Yes, 0.7mm is the typical maximum clearance hole for metric glands (comes from a standard, can't remember which off top of my head)

    When I looked at the documentation for the component certified enclosure ( BAS06ATEX0116U) last night, it doesn't actually give the required information. It refers to another drawing which I didn't see on their website. I wondered if this might be the point where the OP contacted them?

    Then their advice might be correct based on what he told them, or there might have been a misunderstanding.  It all depends on where he lies in the supply chain or end user.