Domestic Battery Storage - G83/G98 - Earthing Arrangements + More

Hi,


I am looking to add a battery storage system to my own home (I am an NICEIC registered contractor, just to make it clear this is a project for myself). This will be a battery only solution, and will not feature any solar arrangements. 


If there are any experts here that can advise on a few questions, that would be superb. 

 
  • GN98 (formally GN83) allows systems up to 16A per phase to be connected without the need for any sort of site inspection before the install (so the solution is notified after). I plan on doing this myself, and I am not part of a microgeneration scheme, but assume self certification is ok, following Part P requirements and issuing the relevant certs to the NIC. 


 

  • The battery I plan on using is the Alpha ESS (combined battery and inverter), which is grid tied with separate backup output(s) for things like lighting circuits and small power circuits. I have a smart meter, however I do not have a feed-in tariff, therefore by means of a CT connected to the battery I plan to set the feed-in to zero using the inverters user interface, so that the battery just delivers power to loads as and when its required. My question here however leads me onto earthing - when running in backup mode, the inverter automatically disconnects the grid and provides power on its dedicated backup connection - what do I do with the Earthing? I am on a TN-C-S supply from the DNO - I would assume an earth rod is required, connected into the MET (as the DNO earthing cannot be relied upon during an outage) which would be combined the DNO earthing (so a rod in the ground connected to the MET and bonded onto the battery inverter). Assuming this is correct, does the inverter need to tie its backup output neutral and earth conductors together, forming its own TN system (it could even be doing this internally I'm not sure and need to check). 


 

  • Anything else I may be missing?



Thanks.

Parents
  • Zoomup:
    vantech:

    The issue with this is that some devices are Class 1 by nature, so would require a "ground" reference for EMC circuits etc - this wouldn't work unless the battery was ground referenced when running on backup. 


    What common typical domestic items would you give as  examples of vulnerable items?

    https://www.bing.com/videos/search?q=what+is+emc&docid=608010981617370857&mid=075EEAE665041D122C8E075EEAE665041D122C8E&view=detail&FORM=VIRE



    Z.




    LED drivers (I have DALI drivers which are all Class 1), server power supplies. They should be OK without it, and agree it could run as an IT system - your idea is good, but I would need to make sure the inverter is 100% isolated from anything that could provide contact with Earth, and this may be impossible. 


Reply
  • Zoomup:
    vantech:

    The issue with this is that some devices are Class 1 by nature, so would require a "ground" reference for EMC circuits etc - this wouldn't work unless the battery was ground referenced when running on backup. 


    What common typical domestic items would you give as  examples of vulnerable items?

    https://www.bing.com/videos/search?q=what+is+emc&docid=608010981617370857&mid=075EEAE665041D122C8E075EEAE665041D122C8E&view=detail&FORM=VIRE



    Z.




    LED drivers (I have DALI drivers which are all Class 1), server power supplies. They should be OK without it, and agree it could run as an IT system - your idea is good, but I would need to make sure the inverter is 100% isolated from anything that could provide contact with Earth, and this may be impossible. 