The Regulation is not referring to the total load but for typical poor design
The regulation falls under the heading of PROTECTION AGAINST OVERLOAD CURRENT.
It is impossible to design in good use of a ring final circuit as it is impossible to determine just what the user will plug in and where.
Z.
perspicacious:
I suppose that the overloading could occur in say a commercial kitchen in a restaurant or pub.
The Regulation is not referring to the total load but for typical poor design where the CU is in the kitchen or utility room and the route of the cable calls in first to heavy loading and then wanders off round the house (or rest of room) before returning to CU.
Do we have rings in commercial kitchens?
At this stage, I am going to retire with terminal embarrassment. Double socket in utility room about 4 ft from CU. Washing machine and tumble drier plugged in.
perspicacious:
Hello Chris
This quote I suppose that the overloading could occur in say a commercial kitchen in a restaurant or pub.is Zoom's, hence my italicisation of it!
Twenty years ago I inspected and tested some 50 or so pubs and couldn't believe that a manufacturer made a twin deep fat fryer each having a 3 kW element and it came with two separate 13 A plugs. These would inevitably be plugged into the nearest double socket-outlet. The manufacturer's logic being that they wouldn't sell any if a dedicated 32 A circuit had to be installed as per the traditional cooker.
I also learned to only have packeted condiments with a pub meal ...
Interesting wiring of yours but fairly typical I'm afraid.................
It was just a general question about rings in commercial kitchens. Yes, there must be 13 A sockets at the very least for small equipment, but radial may be a better option.
I wonder whether the fryers' installation instructions specified two single 13 A sockets.
I noticed when I was in Italy once, that those complimentary bowls of nuts in bars always had a teaspoon so that customers kept their fingers out.
I do not quite see how my wiring could be any different - the CU is where it is and where else would you put the washing machine and tumble drier? Once again, radial may be the better option.