OlympusMons:
Hi Mike, in your example the leg carrying 27A would be running hot, perhaps 70 deg C, therefore would have higher resistivity than the cooler longer leg. I can't do the maths but would this make a huge difference?
i found this calculator Temperature Coefficient of Resistance (gsu.edu) and plugging in a few numbers gives a rise in resistance of 20% for copper, initial temp 20, final temp 70. So in Mike's example above the worst case first leg of the ring of length 1M would have an equivalent length running at 70 deg C of 1.2 Metres, so hardly any difference at all to the load sharing calculations.
OlympusMons:
Hi Mike, in your example the leg carrying 27A would be running hot, perhaps 70 deg C, therefore would have higher resistivity than the cooler longer leg. I can't do the maths but would this make a huge difference?
Now there's a thing. The ring could be self current regulating. The short hot insulated overloaded length has an increase in electrical resistance so the supply shifts to the longer leg.
Z.
OlympusMons:
Yes Zoomup, I saw your post on the old forum about this and wondered if it would have much effect, apparently not in Mike's example, if my sums are correct. The increase in resistance with the constraint of keeping max temp at 70 Deg C doesn't have enough leeway for self-regulation it seems. Good point though.
I would like somebody to offer empirical evidence of any thermal cable damage to a 2.5mm2 P.V.C. cable on a ring final circuit where a socket is positioned close to a consumer unit and heavily loaded. Anyone?
A one degree rise in temperature of copper = a 0.393 per cent rise in electrical resistance.
A 2m length of 2.5mm2 copper conductor carrying approx. 27 Amps will create approx. 10 Watts of heat.
Z.
mapj1:
The assumpmtion is about bunching. The worse case is when all the load is near one end, say within the first 10% of one of the limbs.
By the miracle of resistance scaling with length of cable, and the voltage drop from origin to load being the same both the long and short way round, the current split is always in inverse proportion to the ratio of the lengths.
So if the load is equally far from each end, then the load is shared perfectly, and 16A goes each way.
But let us consider an example of the bad layout case..
It is possible to have say 3 sockets each pulling 10A at 1m, 2m and 5m from the origin and then a 20m return leg with no load.
Now the first 10 amps is spit in the ratio of 1/25 to 24/25, those being the tow path lengths to that socket.
The second 10A is split 2/25 to 23/25
the third 5/25 and 20/25
So as the common denominator is 25ths of 10A is 400mA 'units'
Going left we have (24+23+20)* 0.4A = 26.8 amps
going right we have (1+2+5)* 400mA = 3.2A
Quick sanity check total = 30A.
So that last metre of cable from CU to first socket takes nearly 27A, and would be fine in plaster or clipped direct, but may age rather faster than we would like in thick insulation. It is the only stressed cable on the ring, and making it longer, or moving one load to the return leg would restore order, as would making that first socket a spur off the MCB, so its current is not adding to the short leg current.
(This is often a quicker fix)
If you can avoid having more than one socket in the first 20% of the ring length on either end, the the problem vanishes even in quite thick insulation.
Mike.
At the risk of appearing to be a dissenter, I can not believe that most sparks installing a ring final even bother to consider the positioning of sockets regarding equal loading. Has unequal loading even been shown to cause cable thermal damage?
Having just re-read 433.1.204 I have concluded that the reg. is not about bunching of sockets or having them too close to the origin of the ring final circuit. The reg. is concerned with ring final circuits with or without unfused spurs. That is why the reg. requires that the load current in any part of the circuit (in ring or unfused spur) is "unlikely to exceed for long periods the current carrying capacity of the cable." This is especially important for unfused spurs. That is the main point being made.
I do seem to be a dissenter. Oh ek!