This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Determining Max Zs For Time Current Curve

Former Community Member
Former Community Member
How do you determine the max Zs when the manufacturer does not list or specify the maximum permitted earth fault loop impedance? TN system.


https://library.industrialsolutions.abb.com/publibrary/checkout/GES-6119D?TNR=Time%20Current%20Curves%7CGES-6119D%7CPDF&filename=GES6119.pdf
Parents
  • Don't forget Cmin these days. 411.4.4's requirement is that Zs x Ia ≤ Uo x Cmin.


    Where Ia is the current causing automatic operation of the device in the required time, and for a conventional DNO supply Cmin is 0.95.


       - Andy.
Reply
  • Don't forget Cmin these days. 411.4.4's requirement is that Zs x Ia ≤ Uo x Cmin.


    Where Ia is the current causing automatic operation of the device in the required time, and for a conventional DNO supply Cmin is 0.95.


       - Andy.
Children
No Data