Hi there can anyone point me to and specific regulations that highlight the requirements for working on 11kV?


I’m specifically looking at an 11kV switch disconnector on a TX but would be good to know if this is the same for an RMU.  


Parents
  • IEEE 1584 is a standard for working out arc flash and incident energy. This allows you to calculate the rating of protective clothing you need such that the blast from a short circuit is reasonably survivable. At 1m distance, you will be within the arc produced by a short circuit. 

    “An arc flash has the blast energy of several sticks of dynamite, and a temperature hotter than the surface of the sun”. 


    Regards,


    Alan.
Reply
  • IEEE 1584 is a standard for working out arc flash and incident energy. This allows you to calculate the rating of protective clothing you need such that the blast from a short circuit is reasonably survivable. At 1m distance, you will be within the arc produced by a short circuit. 

    “An arc flash has the blast energy of several sticks of dynamite, and a temperature hotter than the surface of the sun”. 


    Regards,


    Alan.