Overloaded fused spur, opinion please

I was an industrial electrician and have now come across a domestic wiring issue where nothing appeared wrong with the installation.  Those with more experience will have probably have come across this many times.


The kitchen is supplied by a 2.5mm T&E ring fed from a B32 circuit breaker.  On this ring there is a 13A fused switched spur above the worktop feeding a double socket underneath via 2.5 T&E.  There is a washing machine and a dishwasher plugged into this double socket.  Every so often, I assume when both appliances are heating at the same time, the 13A fuse in the spur blows.  The cable supplying this double socket is in the wall so the current-carrying capacity appears to be 18.5A so this was probably being overloaded as well.


I understand that in the regs diversity covers some aspects of this situation, but this specific situation must occur often surely?  The switched spur gives the ability to switch off the appliance easily without having to pull it out in order to reach the switch, so is surely desirable?


In this case I have installed a second switched fused spur feeding a single socket and converted the other to a single.


Is this a common problem in kitchens?
Parents
  • I am not sure but a fused spur off a ring has cartain conditions , and i think one of them is ,it must be a single socket. But useful thread I didnt know twins are rated 13A combined , so logic must be you should never overload a twin beyond 13A.

    As a learner in electrical installation , for a long time I thought rings were a really good idea , and I guess in the days when electrical goods werent efficienct and could draw high currents , rings were the solution , but with goods having electrical efficiency , I think installtion thinking might be better off with radials in part because I can see electrical heating comming along , I have done my own house (a not very thermal efficient one) to fullyy electric and it can come with some eye watering winter bills , but a well designed new build should easily be managable on electricity.
Reply
  • I am not sure but a fused spur off a ring has cartain conditions , and i think one of them is ,it must be a single socket. But useful thread I didnt know twins are rated 13A combined , so logic must be you should never overload a twin beyond 13A.

    As a learner in electrical installation , for a long time I thought rings were a really good idea , and I guess in the days when electrical goods werent efficienct and could draw high currents , rings were the solution , but with goods having electrical efficiency , I think installtion thinking might be better off with radials in part because I can see electrical heating comming along , I have done my own house (a not very thermal efficient one) to fullyy electric and it can come with some eye watering winter bills , but a well designed new build should easily be managable on electricity.