perspicacious:
use a 20 A DP switch to supply the under-counter socket-outlet ... and not an SFCU.
If a 20 A accessory is suitable for use on a 32 A RFC, why do people use a 30/32 A JB on a RFC?
Regards
BAD
BS 1363 socket-outlets are rated 13 A, as are FCUs, so I don't follow the argument fully ... although I guess it supports the query.
The only answer I can give is "always been done that way" - and of course, permits an unfused "spur" to be connected into the ring, whereas the terminals in a 20 A JB would be overloaded by 3x2.5 ?
Would we be happy extending 2.5 sq mm conductors using Wago 773's on an RFC?
perspicacious:
use a 20 A DP switch to supply the under-counter socket-outlet ... and not an SFCU.
If a 20 A accessory is suitable for use on a 32 A RFC, why do people use a 30/32 A JB on a RFC?
Regards
BAD
BS 1363 socket-outlets are rated 13 A, as are FCUs, so I don't follow the argument fully ... although I guess it supports the query.
The only answer I can give is "always been done that way" - and of course, permits an unfused "spur" to be connected into the ring, whereas the terminals in a 20 A JB would be overloaded by 3x2.5 ?
Would we be happy extending 2.5 sq mm conductors using Wago 773's on an RFC?