Overloaded fused spur, opinion please

I was an industrial electrician and have now come across a domestic wiring issue where nothing appeared wrong with the installation.  Those with more experience will have probably have come across this many times.


The kitchen is supplied by a 2.5mm T&E ring fed from a B32 circuit breaker.  On this ring there is a 13A fused switched spur above the worktop feeding a double socket underneath via 2.5 T&E.  There is a washing machine and a dishwasher plugged into this double socket.  Every so often, I assume when both appliances are heating at the same time, the 13A fuse in the spur blows.  The cable supplying this double socket is in the wall so the current-carrying capacity appears to be 18.5A so this was probably being overloaded as well.


I understand that in the regs diversity covers some aspects of this situation, but this specific situation must occur often surely?  The switched spur gives the ability to switch off the appliance easily without having to pull it out in order to reach the switch, so is surely desirable?


In this case I have installed a second switched fused spur feeding a single socket and converted the other to a single.


Is this a common problem in kitchens?
Parents
  • I'm on about mechanical overloading - BS 1363  specifically requires that the input terminals of socket-outlets and FCUs for sol (Class I and Class II stranded conductors) are suitable for 3 no. 2.5 sq mm conductors ...


    BS 5733 if memory serves for the 20 A DP switch.


    433.1.204 is permissive, but doesn't prohibit other arrangements .. if the 20 A DP switch supplies only a single socket-outlet, surely overload current protection is not necessary as per 433.3.1 (ii).


    Surely, we don't want to tie ourselves in knots and conclude that it's not feasible to supply a tumble dryer in a kitchen from an RFC, in one of our devolved nations, unless the socket-outlet that it is connected into is located above the counter? Or do we?
Reply
  • I'm on about mechanical overloading - BS 1363  specifically requires that the input terminals of socket-outlets and FCUs for sol (Class I and Class II stranded conductors) are suitable for 3 no. 2.5 sq mm conductors ...


    BS 5733 if memory serves for the 20 A DP switch.


    433.1.204 is permissive, but doesn't prohibit other arrangements .. if the 20 A DP switch supplies only a single socket-outlet, surely overload current protection is not necessary as per 433.3.1 (ii).


    Surely, we don't want to tie ourselves in knots and conclude that it's not feasible to supply a tumble dryer in a kitchen from an RFC, in one of our devolved nations, unless the socket-outlet that it is connected into is located above the counter? Or do we?