Overloaded fused spur, opinion please

I was an industrial electrician and have now come across a domestic wiring issue where nothing appeared wrong with the installation.  Those with more experience will have probably have come across this many times.


The kitchen is supplied by a 2.5mm T&E ring fed from a B32 circuit breaker.  On this ring there is a 13A fused switched spur above the worktop feeding a double socket underneath via 2.5 T&E.  There is a washing machine and a dishwasher plugged into this double socket.  Every so often, I assume when both appliances are heating at the same time, the 13A fuse in the spur blows.  The cable supplying this double socket is in the wall so the current-carrying capacity appears to be 18.5A so this was probably being overloaded as well.


I understand that in the regs diversity covers some aspects of this situation, but this specific situation must occur often surely?  The switched spur gives the ability to switch off the appliance easily without having to pull it out in order to reach the switch, so is surely desirable?


In this case I have installed a second switched fused spur feeding a single socket and converted the other to a single.


Is this a common problem in kitchens?
Parents
  • I`ve always had a preference for a 20A DP switch on a ring (or a radial) for sockets feeding appliances from behind unless easily access, simply for a quick means of urgent disconnection from mains. OK the Regs do not require it but I feel it could, exceptionally, make a difference. I feel certain that the terminals are designed or tested for 32A but visibly they appear the same or similar to socket terminals in the brands I use so I feel happy to do that. I suspect that I could be gtaken to task for using them on a ring.


    As for Bod and his 20A JB, if it were say 25A JB I might be happy but I`m not aware of the existence of readily available ones.


    Just a note about the 3 x 2.5 conductors - a 4.0 radial strictly does not facilitate a 2.5 spur adding by the standard but it is encouraged in the guidance
Reply
  • I`ve always had a preference for a 20A DP switch on a ring (or a radial) for sockets feeding appliances from behind unless easily access, simply for a quick means of urgent disconnection from mains. OK the Regs do not require it but I feel it could, exceptionally, make a difference. I feel certain that the terminals are designed or tested for 32A but visibly they appear the same or similar to socket terminals in the brands I use so I feel happy to do that. I suspect that I could be gtaken to task for using them on a ring.


    As for Bod and his 20A JB, if it were say 25A JB I might be happy but I`m not aware of the existence of readily available ones.


    Just a note about the 3 x 2.5 conductors - a 4.0 radial strictly does not facilitate a 2.5 spur adding by the standard but it is encouraged in the guidance