ebee:
Just a note about the 3 x 2.5 conductors - a 4.0 radial strictly does not facilitate a 2.5 spur adding by the standard but it is encouraged in the guidance
It's also fair to say that the terminal performance in BS 1363 is a minimum requirement, a manufacturer may make their terminals suitable for other configurations that exceed BS 1363 requirements.
ebee:
Just a note about the 3 x 2.5 conductors - a 4.0 radial strictly does not facilitate a 2.5 spur adding by the standard but it is encouraged in the guidance
It's also fair to say that the terminal performance in BS 1363 is a minimum requirement, a manufacturer may make their terminals suitable for other configurations that exceed BS 1363 requirements.