Overloaded fused spur, opinion please

I was an industrial electrician and have now come across a domestic wiring issue where nothing appeared wrong with the installation.  Those with more experience will have probably have come across this many times.


The kitchen is supplied by a 2.5mm T&E ring fed from a B32 circuit breaker.  On this ring there is a 13A fused switched spur above the worktop feeding a double socket underneath via 2.5 T&E.  There is a washing machine and a dishwasher plugged into this double socket.  Every so often, I assume when both appliances are heating at the same time, the 13A fuse in the spur blows.  The cable supplying this double socket is in the wall so the current-carrying capacity appears to be 18.5A so this was probably being overloaded as well.


I understand that in the regs diversity covers some aspects of this situation, but this specific situation must occur often surely?  The switched spur gives the ability to switch off the appliance easily without having to pull it out in order to reach the switch, so is surely desirable?


In this case I have installed a second switched fused spur feeding a single socket and converted the other to a single.


Is this a common problem in kitchens?
Parents
  • perspicacious:

    Wago 773-104

    Max 2,5 cable

    Terminal current rating 24 A


    However, Table 4D5 Method C for 2.5 cable gives 27 A


    27 A > 24 A


    Regards


    BOD


    Your point, I'm guessing, is that 773's are not always suitable for all circuits with 2.5 sq mm cables ... but that still doesn't answer RFC's.


    For 2.5/1.5 cable, Reference Methods 100, 102, A and C are permitted for 32 A mcb/RCBO, or 32 A BS 88-2 or 88-3 fuses.


    From 4D5 for 2.5, Reference Methods 100 and 102 are only 21 A, and Reference Method A is only 20 A !


    So is the 773 suitable for RFC's?


Reply
  • perspicacious:

    Wago 773-104

    Max 2,5 cable

    Terminal current rating 24 A


    However, Table 4D5 Method C for 2.5 cable gives 27 A


    27 A > 24 A


    Regards


    BOD


    Your point, I'm guessing, is that 773's are not always suitable for all circuits with 2.5 sq mm cables ... but that still doesn't answer RFC's.


    For 2.5/1.5 cable, Reference Methods 100, 102, A and C are permitted for 32 A mcb/RCBO, or 32 A BS 88-2 or 88-3 fuses.


    From 4D5 for 2.5, Reference Methods 100 and 102 are only 21 A, and Reference Method A is only 20 A !


    So is the 773 suitable for RFC's?