perspicacious:
Wago 773-104
Max 2,5 cable
Terminal current rating 24 A
However, Table 4D5 Method C for 2.5 cable gives 27 A
27 A > 24 A
Regards
BOD
Your point, I'm guessing, is that 773's are not always suitable for all circuits with 2.5 sq mm cables ... but that still doesn't answer RFC's.
For 2.5/1.5 cable, Reference Methods 100, 102, A and C are permitted for 32 A mcb/RCBO, or 32 A BS 88-2 or 88-3 fuses.
From 4D5 for 2.5, Reference Methods 100 and 102 are only 21 A, and Reference Method A is only 20 A !
So is the 773 suitable for RFC's?
perspicacious:
Wago 773-104
Max 2,5 cable
Terminal current rating 24 A
However, Table 4D5 Method C for 2.5 cable gives 27 A
27 A > 24 A
Regards
BOD
Your point, I'm guessing, is that 773's are not always suitable for all circuits with 2.5 sq mm cables ... but that still doesn't answer RFC's.
For 2.5/1.5 cable, Reference Methods 100, 102, A and C are permitted for 32 A mcb/RCBO, or 32 A BS 88-2 or 88-3 fuses.
From 4D5 for 2.5, Reference Methods 100 and 102 are only 21 A, and Reference Method A is only 20 A !
So is the 773 suitable for RFC's?