perspicacious:
Provided the manufacturer's information shows that the conductor sizes for the terminals are suitable for 2 x 2.5 or 2x 4 sq mm, I don't believe there's a problem. Many of them are suitable for the same conductor configurations as BS 1363 accessories.
Is there any reason to conclude otherwise?
Conclude as opposed to assume? When I contacted several manufacturers years ago asking if their 20 A DP switch input terminals were suitable for connection to a 32 A RFC, of the few that re[plied, their only comment was that the switch was made to BS 5733.
Regards
BOD
Hopefully, then BS EN 60669-1 will sort that out then, per earlier post?
I agree, it's not made easy. The response you received was far from helpful.
perspicacious:
Provided the manufacturer's information shows that the conductor sizes for the terminals are suitable for 2 x 2.5 or 2x 4 sq mm, I don't believe there's a problem. Many of them are suitable for the same conductor configurations as BS 1363 accessories.
Is there any reason to conclude otherwise?
Conclude as opposed to assume? When I contacted several manufacturers years ago asking if their 20 A DP switch input terminals were suitable for connection to a 32 A RFC, of the few that re[plied, their only comment was that the switch was made to BS 5733.
Regards
BOD
Hopefully, then BS EN 60669-1 will sort that out then, per earlier post?
I agree, it's not made easy. The response you received was far from helpful.