Overloaded fused spur, opinion please

I was an industrial electrician and have now come across a domestic wiring issue where nothing appeared wrong with the installation.  Those with more experience will have probably have come across this many times.


The kitchen is supplied by a 2.5mm T&E ring fed from a B32 circuit breaker.  On this ring there is a 13A fused switched spur above the worktop feeding a double socket underneath via 2.5 T&E.  There is a washing machine and a dishwasher plugged into this double socket.  Every so often, I assume when both appliances are heating at the same time, the 13A fuse in the spur blows.  The cable supplying this double socket is in the wall so the current-carrying capacity appears to be 18.5A so this was probably being overloaded as well.


I understand that in the regs diversity covers some aspects of this situation, but this specific situation must occur often surely?  The switched spur gives the ability to switch off the appliance easily without having to pull it out in order to reach the switch, so is surely desirable?


In this case I have installed a second switched fused spur feeding a single socket and converted the other to a single.


Is this a common problem in kitchens?
Parents
  • perspicacious:
    Provided the manufacturer's information shows that the conductor sizes for the terminals are suitable for 2 x 2.5 or 2x 4 sq mm, I don't believe there's a problem. Many of them are suitable for the same conductor configurations as BS 1363 accessories.


    Is there any reason to conclude otherwise?



    Conclude as opposed to assume? When I contacted several manufacturers years ago asking if their 20 A DP switch input terminals were suitable for connection to a 32 A RFC, of the few that re[plied, their only comment was that the switch was made to BS 5733.


    Regards


    BOD


    Hopefully, then BS EN 60669-1 will sort that out then, per earlier post?


    I agree, it's not made easy. The response you received was far from helpful.


Reply
  • perspicacious:
    Provided the manufacturer's information shows that the conductor sizes for the terminals are suitable for 2 x 2.5 or 2x 4 sq mm, I don't believe there's a problem. Many of them are suitable for the same conductor configurations as BS 1363 accessories.


    Is there any reason to conclude otherwise?



    Conclude as opposed to assume? When I contacted several manufacturers years ago asking if their 20 A DP switch input terminals were suitable for connection to a 32 A RFC, of the few that re[plied, their only comment was that the switch was made to BS 5733.


    Regards


    BOD


    Hopefully, then BS EN 60669-1 will sort that out then, per earlier post?


    I agree, it's not made easy. The response you received was far from helpful.