Overloaded fused spur, opinion please

I was an industrial electrician and have now come across a domestic wiring issue where nothing appeared wrong with the installation.  Those with more experience will have probably have come across this many times.


The kitchen is supplied by a 2.5mm T&E ring fed from a B32 circuit breaker.  On this ring there is a 13A fused switched spur above the worktop feeding a double socket underneath via 2.5 T&E.  There is a washing machine and a dishwasher plugged into this double socket.  Every so often, I assume when both appliances are heating at the same time, the 13A fuse in the spur blows.  The cable supplying this double socket is in the wall so the current-carrying capacity appears to be 18.5A so this was probably being overloaded as well.


I understand that in the regs diversity covers some aspects of this situation, but this specific situation must occur often surely?  The switched spur gives the ability to switch off the appliance easily without having to pull it out in order to reach the switch, so is surely desirable?


In this case I have installed a second switched fused spur feeding a single socket and converted the other to a single.


Is this a common problem in kitchens?
Parents
  • gkenyon:
    perspicacious:
    This is the same question re Wago's ? Provided the terminals are sized for either 2x2.5 sq mm or 2x4 sq mm, surely there's not an issue here?


    Until that is answered, there's no point in adding further asides unless a career in politics is looming?


    Again, simply, are the INPUT/loop in terminals of a 20 A DP switch suitable for connection to a 32 A RFC irrespective of whatever is on the OUT terminals?


    Regards


    BOD

     


    Provided the manufacturer's information shows that the conductor sizes for the terminals are suitable for 2 x 2.5 or 2x 4 sq mm, I don't believe there's a problem. Many of them are suitable for the same conductor configurations as BS 1363 accessories.


    Is there any reason to conclude otherwise?


    So, I checked - BS EN 60669-1 is being used for switches now, not the general standard BS 5733.


    20 A switches are tested for temperature rise with a current of 25 A, which is broadly in line with the tests for BS 1363 accessories.




    BS EN 60669-1 and BS 5733 are similar. For accessories > 16 <= 25 A, the terminals must accommodate 1.5 to 4 mm² (5733) or 2.5 - 6 mm² (60669-1) solid conductors. Whilst the terminals may accommodate more conductor, clearly it must still be possible to clamp the smallest one adequately. If a 60669-1 terminal can accommodate a 6 mm² conductor, it seems pretty obvious that it will accommodate 2 x 2.5 mm². Regarding looping in and out, or being placed in a ring, the rating is that of the switch. I see no reason why any terminal which will accommodate 2 x 2.5 mm² should not also safely carry the load (up to 27 A, RM C).


    As Graham says, manufacturer's instructions are what count. Some 20 A switches may be inserted in a ring, some may not.


    My preference is to spur off the nearest socket in 2.5 mm² and put the switch into the spur.


    I would have no reservations about using Wagos of the appropriate rating in an appropriate enclosure. A back box would not be adequate for a fully loaded cable.


Reply
  • gkenyon:
    perspicacious:
    This is the same question re Wago's ? Provided the terminals are sized for either 2x2.5 sq mm or 2x4 sq mm, surely there's not an issue here?


    Until that is answered, there's no point in adding further asides unless a career in politics is looming?


    Again, simply, are the INPUT/loop in terminals of a 20 A DP switch suitable for connection to a 32 A RFC irrespective of whatever is on the OUT terminals?


    Regards


    BOD

     


    Provided the manufacturer's information shows that the conductor sizes for the terminals are suitable for 2 x 2.5 or 2x 4 sq mm, I don't believe there's a problem. Many of them are suitable for the same conductor configurations as BS 1363 accessories.


    Is there any reason to conclude otherwise?


    So, I checked - BS EN 60669-1 is being used for switches now, not the general standard BS 5733.


    20 A switches are tested for temperature rise with a current of 25 A, which is broadly in line with the tests for BS 1363 accessories.




    BS EN 60669-1 and BS 5733 are similar. For accessories > 16 <= 25 A, the terminals must accommodate 1.5 to 4 mm² (5733) or 2.5 - 6 mm² (60669-1) solid conductors. Whilst the terminals may accommodate more conductor, clearly it must still be possible to clamp the smallest one adequately. If a 60669-1 terminal can accommodate a 6 mm² conductor, it seems pretty obvious that it will accommodate 2 x 2.5 mm². Regarding looping in and out, or being placed in a ring, the rating is that of the switch. I see no reason why any terminal which will accommodate 2 x 2.5 mm² should not also safely carry the load (up to 27 A, RM C).


    As Graham says, manufacturer's instructions are what count. Some 20 A switches may be inserted in a ring, some may not.


    My preference is to spur off the nearest socket in 2.5 mm² and put the switch into the spur.


    I would have no reservations about using Wagos of the appropriate rating in an appropriate enclosure. A back box would not be adequate for a fully loaded cable.