This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Overloaded fused spur, opinion please

I was an industrial electrician and have now come across a domestic wiring issue where nothing appeared wrong with the installation.  Those with more experience will have probably have come across this many times.


The kitchen is supplied by a 2.5mm T&E ring fed from a B32 circuit breaker.  On this ring there is a 13A fused switched spur above the worktop feeding a double socket underneath via 2.5 T&E.  There is a washing machine and a dishwasher plugged into this double socket.  Every so often, I assume when both appliances are heating at the same time, the 13A fuse in the spur blows.  The cable supplying this double socket is in the wall so the current-carrying capacity appears to be 18.5A so this was probably being overloaded as well.


I understand that in the regs diversity covers some aspects of this situation, but this specific situation must occur often surely?  The switched spur gives the ability to switch off the appliance easily without having to pull it out in order to reach the switch, so is surely desirable?


In this case I have installed a second switched fused spur feeding a single socket and converted the other to a single.


Is this a common problem in kitchens?
Parents
  • You know that and I know that, but the kitchen “installation managers” that went on the 16th Edition courses to become “qualified” would not have it, so they set the standard for how things are being done.


    One asked me if I had the “Wiring Regulations” certificate. I replied I did and that I also had the 2360 parts one and two, I&T and 2400. He said “It doesn’t matter about those others, so long as you have the Wiring Regulations certificate”.


    Twenty years ago with a box of SFCUs and a Wiring Regulations certificate you were the go to guy for kitchen electrical work  ?
Reply
  • You know that and I know that, but the kitchen “installation managers” that went on the 16th Edition courses to become “qualified” would not have it, so they set the standard for how things are being done.


    One asked me if I had the “Wiring Regulations” certificate. I replied I did and that I also had the 2360 parts one and two, I&T and 2400. He said “It doesn’t matter about those others, so long as you have the Wiring Regulations certificate”.


    Twenty years ago with a box of SFCUs and a Wiring Regulations certificate you were the go to guy for kitchen electrical work  ?
Children
No Data