I was an industrial electrician and have now come across a domestic wiring issue where nothing appeared wrong with the installation.  Those with more experience will have probably have come across this many times.


The kitchen is supplied by a 2.5mm T&E ring fed from a B32 circuit breaker.  On this ring there is a 13A fused switched spur above the worktop feeding a double socket underneath via 2.5 T&E.  There is a washing machine and a dishwasher plugged into this double socket.  Every so often, I assume when both appliances are heating at the same time, the 13A fuse in the spur blows.  The cable supplying this double socket is in the wall so the current-carrying capacity appears to be 18.5A so this was probably being overloaded as well.


I understand that in the regs diversity covers some aspects of this situation, but this specific situation must occur often surely?  The switched spur gives the ability to switch off the appliance easily without having to pull it out in order to reach the switch, so is surely desirable?


In this case I have installed a second switched fused spur feeding a single socket and converted the other to a single.


Is this a common problem in kitchens?
Parents
  • Sparkingchip:


    Just to complicate it more they would also point out that table says plug and sockets don’t provide emergency switching, so even if the socket was accessible you still needed the SFCU, as the SFCU fulfils all three requirements of isolation, emergency switching and functional switching.


    Interesting that a switched socket-outlet can't be used for emergency switching


    Regardless of BS 7671 and BS 1363-2 say, people do use them like that ... so the requirements in BS 7671 don't match the real world. An ordinary person wouldn't have any awareness of the difference, and simply switch off at the socket-outlet (if switched) and unplug a portable appliance if they saw smoke coming out of it.


    Anyway, no-one said that a single device has to be provided to meet all of the requirements.


Reply
  • Sparkingchip:


    Just to complicate it more they would also point out that table says plug and sockets don’t provide emergency switching, so even if the socket was accessible you still needed the SFCU, as the SFCU fulfils all three requirements of isolation, emergency switching and functional switching.


    Interesting that a switched socket-outlet can't be used for emergency switching


    Regardless of BS 7671 and BS 1363-2 say, people do use them like that ... so the requirements in BS 7671 don't match the real world. An ordinary person wouldn't have any awareness of the difference, and simply switch off at the socket-outlet (if switched) and unplug a portable appliance if they saw smoke coming out of it.


    Anyway, no-one said that a single device has to be provided to meet all of the requirements.