ebee:
I did not like the look of his one strand of 1.0mm2 conductor in an ashley JB20A on his security lighting (tungsten halogen) and that`s why I mentioned doubling to him and got his ruf comment.
I am not aware of anyone else agreeing with him
The argument against doubling, or twisting two or more conductors together (using pliers) is that the end of the cable(s) may be damaged.
BS 6220 specifies: Terminals shall be capable of accommodating and clamping at least two conductors two sizes smaller than the designated size, the conductors being solid or stranded. On the basis of a nominal 2.5 mm² conductor size, it follows that your chum's JB has been used appropriately.
ebee:
I did not like the look of his one strand of 1.0mm2 conductor in an ashley JB20A on his security lighting (tungsten halogen) and that`s why I mentioned doubling to him and got his ruf comment.
I am not aware of anyone else agreeing with him
The argument against doubling, or twisting two or more conductors together (using pliers) is that the end of the cable(s) may be damaged.
BS 6220 specifies: Terminals shall be capable of accommodating and clamping at least two conductors two sizes smaller than the designated size, the conductors being solid or stranded. On the basis of a nominal 2.5 mm² conductor size, it follows that your chum's JB has been used appropriately.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site